Abstract—The phenomenon of overvoltage at motor terminals from serious insulation damage leading ultimately to failure.
in long-cable-fed PWM AC drives poses a severe stress on Additionally, NEMA has suggested that / be limited
motor insulation systems. The overvoltage is typically caused to less than 500 / for general-purpose motors in the
by the high change rate of the inverter output voltage ( / ) 460V class [6].
and the surge impedance mismatch between the inverter,
connecting power cable and the motor. This paper presents a Accordingly, this paper presents a survey of the state-of-
comparative survey of the existing methods of overvoltage the-art methods for overvoltage suppression caused by such
suppression, which includes passive filters at both motor high / and surge impedance mismatch in PWM AC
terminals and inverter terminals. The design methodologies, drives. The paper aims at providing an encompassing
effectiveness, and practical applicability of these passive filters reference for industrial users to select the most appropriate
are discussed through computer simulations based on mitigation technique.
Ansys/Simplorer 9.0, and the promising approaches are
recommended for researchers and industrial users. Section II analyzes the cause of overvoltage at motor
terminals. Section III gives the detailed review of passive
I. INTRODUCTION filters at motor terminals and inverter terminals. Simulation
results of these passive filters are discussed and compared in
One of the remarkable advancements in power switching
Section IV. Finally, conclusions are presented in Section V.
devices has been the increasing speeds of switching and
related switching frequencies, in addition to the associated II. ANALYSIS OF OVERVOLTAGE AT MOTOR TERMINALS
high-frequency operation of PWM AC drives. This results in
a more sinusoidal motor current waveform with less ripple, Overvoltages at motor terminals are determined by three
less copper losses, and less switching losses. However, the main aspects, namely, the rise time of the PWM pulses, the
consequent high rate of voltage rise, / , has adverse cable length, and the impedance mismatch between the
effects on motor insulation systems and contributes to inverter, power cable, and the motor. Most often, the cable
bearing current problems [1]-[4]. Moreover, in some length interconnecting the power converter and the motor is
industrial applications, constraints are such that the motor dictated by the specific layout of an industry installation and
and the PWM inverter have to be placed at separate locations, therefore we may have no choice in this matter, thus, what
thus long interconnecting cables are often required between we can mitigate or compensate for is the impedance
them. As presented in [1], narrow PWM pulses traveling on mismatch and the rise time of the inverter output pulses,
long cables from the inverter to the motor behave like which determine two categories of mitigation methods for
traveling waves on transmission lines, in which a overvoltage in long-cable-fed PWM AC drives.
phenomenon of voltage reflection and possibly successive A. Impedance mismatch
voltage reflection leading to overvoltage at the motor
Surge impedance mismatch between the inverter, power
terminals will occur. Actually, the associated voltage
cable, and the motor is the most direct reason leading to
reflection is a function of the inverter output pulse rise time,
voltage reflection at the motor terminals. The reflected
and the length of the motor cables as well as the surge
voltage that is superposed on the motor terminal is the
impedances of the motor and cable systems [3], [4]. If the
incident dc-link voltage multiplied by the reflection
pulses take longer than one-third the rise time to travel from
coefficients at the motor terminal, Γ , and at the inverter
the inverter to the motor, then a full reflection will occur at
terminal, Γ , respectively, which can be defined as [3]:
the motor terminals and the pulse amplitude will
approximately double [5]. In this case, if no mitigation Z Z
measures are implemented, the motor would likely suffer ΓM = (1)
Z Z
The work was partially supported by NSF under grant No. 1028348.
where, Z is the motor surge impedance, Z , is the surge Thus, if 20% overshoot is the maximum overvoltage allowed
impedance of the voltage source inverter (typically Z 0), at the motor terminals, it follows that, the critical rise time of
and Z is the cable surge impedance given by [3]: the PWM pulses can be calculated as
M
L =0.2 (9)
Z = (3)
C
M
t = (10)
where, L , is the cable inductance per unit length, and C , is
the cable capacitance per unit length. Generally, if Z
To verify this conclusion, a simulation of a 5-hp 460-V
0, it follows that, ΓS 1, and the overvoltage magnitude is
induction motor drive system based on Simplorer 9.0 was
primarily determined by ΓM .
conducted here, and the simulation schematic was shown in
B. Rise time of PWM pulses Fig.1. Assuming the cable length is =50m feeding an
According to wave propagation theory and voltage induction motor with ΓM 0.9 (typical value for motors of
reflection analysis, a propagation delay for the inverter less than 20 hp). The parameters of the cable are shown in
output PWM pulses to travel from the inverter terminals to Table I, hence can be computed as follows:
the motor terminals can be expressed as 1 1
= =
= (4) √0.34 10 181 10
= 1.27 10 / (11)
where is the cable length, and is the pulse propagation Accordingly,
velocity in the motor cable and is given by [2]:
M
t =
= (5)
.
As stated in [7], the forward-travelling inverter output = .
pulses will be reflected at the motor terminals after
propagation delay, t , and then the resulting backward- = 5.31 µs (12)
traveling wave, which is a function of ΓM , moving toward Fig.2 shows the normalized line voltages at the inverter
the inverter, will also be reflected at the inverter terminals in terminals and motor terminals with different rise time of
the same manner. Hence, after the PWM pulses has travelled PWM pulses. It demonstrates that the voltage amplitude at
the cable length three times, the peak voltage, VLL, , can be the motor terminals sensitively changes with the rise time of
shown to be [7]: PWM pulses. At rise time, t = 0.1µs, the voltage overshoot
V M
of the motor terminal reaches as high as 85% of the inverter
VLL, = +V , for (6) terminal voltage. However, at a critical time, t = 5.31µs,
the voltage overshoot of the motor terminal is close to 20%
VLL, = V ΓM +V , for (7) of the inverter terminal voltage. At rise time, t = 6µs, the
motor terminal voltage is almost equal to the inverter
where, V and t represent the dc-bus voltage and rise terminal voltage. These simulation results indicate that the
time of PWM pulses respectively. overvoltage at the motor terminals can be mitigated by
increasing the rise time of the inverter output pulses, such as
Then, for a longer rise time of PWM pulses, (i.e., t ), through the use of / flattening filters.
the normalized peak voltage can be expressed as
Figure 1. Simulation schematic of a 5-hp 460-V induction motor drives with 50m cable interconnecting the inverter and the motor.
2161
TABLE I. CABLE PER-METER PARAMETERS
(a)
Z =Z = + = (13)
III. PASSIVE FILTERS TOPOLOGIES where is the “lumped parameter” cable inductance.
From the point of view of flattening / of the PWM The parameters of the LC filter can be determined from
pulses, there are mainly two mitigation methods: one is using the solution of (13) and (14).
active filters, but this method is seldom employed in
industrial motor drives since additional switches and B. RLC filter at the motor terminal
complex algorithms are required. In the other approach, one Similarly, a second-order RLC filter, as shown in Fig.4,
uses passive filters based on resistors, inductors and has also been proposed to suppress the overvoltage at the
capacitors. The latter one is much more popular because of motor terminals [5], [10], [11]. The filter parameters are
its simplicity and availability. selected such that the equivalent impedance of the filter
Passive filters, such as RC and RLC filters, have been closely matches the surge impedance of the cable. Therefore,
proposed to be installed at the motor terminals to match the one can write:
surge impedance of the cable, which could significantly 1
attenuate the overvoltage at the motor terminals. On the other = +
+
hand, for some special applications, such as submarine
situations or deep well pumps, filters have to be installed at
= + (15)
2162
Here, the magnitude of should be equal to the cable reason, these filters are often designed with a resonant
surge impedance, Z , accordingly, from (15), one can write: frequency significantly below the switching frequency, and
above the output fundamental frequency to avoid resonance
with the load, as expressed in (18):
Z = + + (16)
= (18)
Again, the resistor R is designed to result in an over where,
damped circuit, thus:
(19)
LC
R (17)
C Here, , , and , are the filter resonance frequency,
Since a cable’s surge impedance (characteristic switching frequency, and fundamental frequency of the
impedance), Z , is independent of the cable length, it follows drive’s output voltage, respectively.
that, the filter design should be the same for a given cable
regardless of the cable length.
In addition, according to [5], it is recommended that, the
resonant frequency of the filter be selected to be five times
the switching frequency of the PWM inverter. Moreover, the
operating frequency of the RLC filter should be chosen to be
near the resonant frequency to minimize the voltage
overshoot. Figure 6. LC filter at the inverter terminal.
(b)
2163
However, the physical size and power losses of the can be seen, there is almost no voltage overshoot because of
traditional filters shown in Fig.7 are considerable because of the clamping effect of diode bridges.
the introduction of resistors. A low-loss LC filter clamped by
Table II summarizes the quantities and qualities of the
diode bridges, as shown in Fig.8, has been put forward in
components parameters, voltage overshoots, and power
[18]-[20]. For this filter, the LC resonating voltage is
losses of the filters discusses above. These results are briefly
clamped to the dc-bus voltage by virtue of the fast recovery
discussed in the conclusions.
diodes, and the rising time of inverter output voltage can be
controlled by the values of L and C of the filter. Compared
with the traditional LC filters the physical dimensions of
diode clamping filters are smaller. Moreover, the power
losses in the clamping circuit are decreased in comparison to
the losses in the damping resistors of Fig.7.
2164
Figure 13. Line voltages at inverter and motor terminals with reactor at the Figure 14. Line voltages at inverter and motor terminals with LC filter at
inverter for a 460-V 5-hp 5-kHz induction motor drive fed by 90m-cable. the inverter for 460-V 5-hp 5-kHz induction motor drive fed by 90m-cable.
Figure 15. Line voltages at the inverter and motor terminals with LC clamp filters at the inverter output
for a 460-V 5-hp 5-kHz induction motor drive fed by 90m-cable.
Comparative Various types of passive filters for 3-phase 460-V 5-hp induction motor fed by 90m cable (assuming = . )
factors RC filter @ motor RLC filter @ motor Reactor @ inverter LC filter @ inverter RLC filter @ inverter Clamp filter @ inverter
Resistors 43Ω 125 Ω ---- ---- 43Ω ----